    Ed,

    Never under estimate an engineers ability to add complexity!

    What is wrong with the simple notion of % full and capacity total in MW and storage ratio?!?!  Completely agnostic to the storage device characteristics!!!

    If I know the storage is 60% full and has a total capacity of 100 MW - and a default ratio of power to storage of 4:1 then I know I can push 40 x 4 = 160 MW at the device to fill it.  Plus if device is sending out updating in intervals - I might send it 100MW - then it says it is 85% full - so I adjust accordingly.

    Once it is full it sends "Stop!" - simple!

    If you want to get clever on your backend systems - you may track actual storage ratio achieved compared to default - or the device can adjust that itself.

    Thanks, DW

    -------- Original Message --------
    Subject: RE: [emix] Power storage strategies
    From: "Edward Cazalet" <ed@MegaWattSF.com>
    Date: Mon, April 26, 2010 12:04 pm
    To: "'David RR Webber (XML)'" <david@drrw.info>, "'Phil Davis'"
    <pddcoo@gmail.com>
    Cc: <emix@lists.oasis-open.org>, <Toby.Considine@gmail.com>

    Phil and David,
    Yes, storage can play a big role in providing ancillary services and supporting the integration of wind and solar.  I am a big advocate of distributed storage in very large amounts (see my attached editorial on the subject which has led to pending legislation to promote storage in California).  Also see my storage company's website (www.megawattsf.com) below on this subject.
    Both of you raise the issue of what is behind the meters including storage.  After thinking about this problem for some time, I think it is too difficult to communicate what is physically behind the meters.  We would need to know the state of charge of storage devices,  the charge/discharge efficiencies and nonlinearities of each type of battery, battery temperature that can limit use,  and the opportunity costs of storage use.  In some case what is behind the meter changes such as when an electric vehicle is plugged in,  a storage battery is added or removed for maintenance and so on.  And sometimes the storage may be ice storage which is useful when there is an air conditioning load and less useful when there is not air conditioning load. And as David said, each storage device needs new XML.
    The other approach is Transactional Energy, wherein the priced offers and transactions over current and forward intervals using frequent, small transactions can fully convey all of the necessary transactional information on what is behind the meter including any storage with no specifics on the devices or their state and no special XML.  And with forward priced offers that form a forward price curve, automated self-dispatch of storage  is much easier to do.
    Ed
    Edward G. Cazalet, Ph.D.
    Vice President and Co-Founder
    MegaWatt Storage Farms, Inc.
    101 First Street, Suite 552
    Los Altos, CA 94022
    650-949-5274
    cell: 408-621-2772
    From: David RR Webber (XML) [mailto:david@drrw.info]
    Sent: Monday, April 26, 2010 8:42 AM
    To: Phil Davis
    Cc: emix@lists.oasis-open.org; Toby.Considine@gmail.com
    Subject: RE: [emix] Power storage strategies
    Phil,
    Can we get one of those 400 people to write some XML for us?!?!
     ; -)
    If telephone switch industry is a guide here - this means we already have 3 sets of battery subsystem XML - GE, Hitachi and Samsung - with more to follow.  And of course each new model has new XML...

    Thanks, DW

    -------- Original Message --------
    Subject: RE: [emix] Power storage strategies
    From: "Phil Davis" <pddcoo@gmail.com>
    Date: Mon, April 26, 2010 11:26 am
    To: "'David RR Webber (XML)'" <david@drrw.info>,
    <Toby.Considine@gmail.com>
    Cc: <emix@lists.oasis-open.org>

    Actually, GE announced such a system last week and is hiring 400 people in Atlanta to staff the new business. It's a substation level product.  Also, I have spoken personally with people at Hitachi and Samsung who are testing a 1 MW battery.  Such a battery from another vendor is in test operation behind PJM's main offices. So local here takes on a new meaning depending on whether it is truly behind the customer meter, or behind the distribution grid meters (substations and the like), or on a transmission system.  Theoretically, batteries of this size could replace generators used for voltage or frequency support.
     
    Phil Davis

    From: David RR Webber (XML) [mailto:david@drrw.info]
    Sent: Monday, April 26, 2010 10:58 AM
    To: Toby.Considine@gmail.com
    Cc: emix@lists.oasis-open.org
    Subject: [emix] Power storage strategies

    Toby,
    It occurs to me that local storage can potentially play a role here - depending on its efficiency of course.  One can anticipate that future technology will offer higher % there - especially if market forces drive that equation.
    Therefore - a future system could offset power surges by drawing on locally stored resources that were captured during off-peak or excess capacity.  In fact such a system may notify suppliers that they can "push" excess power to local storage at some pre-determined cost point - and of course also need to indicate that the storage facility is at a certain % level, or if empty - accept units at a higher cost rate.
    DW

    ________________________________________________________________________
    This email has been scanned for SPAM content and Viruses by the MessageLabs Email Security System.
    ________________________________________________________________________
    --------------------------------------------------------------------- To unsubscribe from this mail list, you must leave the OASIS TC that generates this mail. Follow this link to all your TCs in OASIS at: https://www.oasis-open.org/apps/org/workgroup/portal/my_workgroups.php
    --------------------------------------------------------------------- To unsubscribe from this mail list, you must leave the OASIS TC that generates this mail. Follow this link to all your TCs in OASIS at: https://www.oasis-open.org/apps/org/workgroup/portal/my_workgroups.php


  • 2.  RE: [emix] Power storage strategies

    Posted 04-26-2010 16:44

    Push?

    Will that work as well as the Push technologies that are perennially the next wave on the ‘net

    The correct push is appropriate pricing.

    The correct measure of battery efficiency vs afternoon scarcity is pricing.

    tc


    "If something is not worth doing, it`s not worth doing well" - Peter Drucker


    Toby Considine
    TC9, Inc

    OASIS Technical Advisory Board
    TC Chair: oBIX & WS-Calendar

    TC Editor: EMIX, EnergyInterop

      

    Email: Toby.Considine@gmail.com
    Phone: (919)619-2104

    http://www.tcnine.com/
    blog: www.NewDaedalus.com

    From: David RR Webber (XML) [mailto:david@drrw.info]
    Sent: Monday, April 26, 2010 12:36 PM
    To: Edward Cazalet
    Cc: emix@lists.oasis-open.org; Toby.Considine@gmail.com; 'Phil Davis'
    Subject: RE: [emix] Power storage strategies

    Ed,

    Never under estimate an engineers ability to add complexity!

    What is wrong with the simple notion of % full and capacity total in MW and storage ratio?!?!  Completely agnostic to the storage device characteristics!!!

    If I know the storage is 60% full and has a total capacity of 100 MW - and a default ratio of power to storage of 4:1 then I know I can push 40 x 4 = 160 MW at the device to fill it.  Plus if device is sending out updating in intervals - I might send it 100MW - then it says it is 85% full - so I adjust accordingly.

    Once it is full it sends "Stop!" - simple!

    If you want to get clever on your backend systems - you may track actual storage ratio achieved compared to default - or the device can adjust that itself.

    Thanks, DW

    -------- Original Message --------
    Subject: RE: [emix] Power storage strategies
    From: "Edward Cazalet" <ed@MegaWattSF.com>
    Date: Mon, April 26, 2010 12:04 pm
    To: "'David RR Webber (XML)'" <david@drrw.info>, "'Phil Davis'"
    <pddcoo@gmail.com>
    Cc: <emix@lists.oasis-open.org>, <Toby.Considine@gmail.com>

    Phil and David,

     

    Yes, storage can play a big role in providing ancillary services and supporting the integration of wind and solar.  I am a big advocate of distributed storage in very large amounts (see my attached editorial on the subject which has led to pending legislation to promote storage in California).  Also see my storage company's website (www.megawattsf.com) below on this subject.

     

    Both of you raise the issue of what is behind the meters including storage.  After thinking about this problem for some time, I think it is too difficult to communicate what is physically behind the meters.  We would need to know the state of charge of storage devices,  the charge/discharge efficiencies and nonlinearities of each type of battery, battery temperature that can limit use,  and the opportunity costs of storage use.  In some case what is behind the meter changes such as when an electric vehicle is plugged in,  a storage battery is added or removed for maintenance and so on.  And sometimes the storage may be ice storage which is useful when there is an air conditioning load and less useful when there is not air conditioning load. And as David said, each storage device needs new XML.

     

    The other approach is Transactional Energy, wherein the priced offers and transactions over current and forward intervals using frequent, small transactions can fully convey all of the necessary transactional information on what is behind the meter including any storage with no specifics on the devices or their state and no special XML.  And with forward priced offers that form a forward price curve, automated self-dispatch of storage  is much easier to do.

     

    Ed

     

     

    Edward G. Cazalet, Ph.D.

    Vice President and Co-Founder

    MegaWatt Storage Farms, Inc.

    101 First Street, Suite 552

    Los Altos, CA 94022

    650-949-5274

    cell: 408-621-2772

     

    From: David RR Webber (XML) [mailto:david@drrw.info]
    Sent: Monday, April 26, 2010 8:42 AM
    To: Phil Davis
    Cc: emix@lists.oasis-open.org; Toby.Considine@gmail.com
    Subject: RE: [emix] Power storage strategies

     

    Phil,

     

    Can we get one of those 400 people to write some XML for us?!?!

     

     ; -)

     

    If telephone switch industry is a guide here - this means we already have 3 sets of battery subsystem XML - GE, Hitachi and Samsung - with more to follow.  And of course each new model has new XML...

     

    Thanks, DW

    -------- Original Message --------
    Subject: RE: [emix] Power storage strategies
    From: "Phil Davis" <pddcoo@gmail.com>
    Date: Mon, April 26, 2010 11:26 am
    To: "'David RR Webber (XML)'" <david@drrw.info>,
    <Toby.Considine@gmail.com>
    Cc: <emix@lists.oasis-open.org>

    Actually, GE announced such a system last week and is hiring 400 people in Atlanta to staff the new business. It's a substation level product.  Also, I have spoken personally with people at Hitachi and Samsung who are testing a 1 MW battery.  Such a battery from another vendor is in test operation behind PJM's main offices. So local here takes on a new meaning depending on whether it is truly behind the customer meter, or behind the distribution grid meters (substations and the like), or on a transmission system.  Theoretically, batteries of this size could replace generators used for voltage or frequency support.

     

    Phil Davis

     


    From: David RR Webber (XML) [mailto:david@drrw.info]
    Sent: Monday, April 26, 2010 10:58 AM
    To: Toby.Considine@gmail.com
    Cc: emix@lists.oasis-open.org
    Subject: [emix] Power storage strategies

    Toby,

     

    It occurs to me that local storage can potentially play a role here - depending on its efficiency of course.  One can anticipate that future technology will offer higher % there - especially if market forces drive that equation.

     

    Therefore - a future system could offset power surges by drawing on locally stored resources that were captured during off-peak or excess capacity.  In fact such a system may notify suppliers that they can "push" excess power to local storage at some pre-determined cost point - and of course also need to indicate that the storage facility is at a certain % level, or if empty - accept units at a higher cost rate.

     

    DW

     

     


    ________________________________________________________________________
    This email has been scanned for SPAM content and Viruses by the MessageLabs Email Security System.
    ________________________________________________________________________
    --------------------------------------------------------------------- To unsubscribe from this mail list, you must leave the OASIS TC that generates this mail. Follow this link to all your TCs in OASIS at: https://www.oasis-open.org/apps/org/workgroup/portal/my_workgroups.php

    --------------------------------------------------------------------- To unsubscribe from this mail list, you must leave the OASIS TC that generates this mail. Follow this link to all your TCs in OASIS at: https://www.oasis-open.org/apps/org/workgroup/portal/my_workgroups.php



  • 3.  RE: [emix] Power storage strategies

    Posted 04-26-2010 18:32
    
    
    
    
    
    
    
    Agree that we should be generic.  The real data of significance is available rate of charge/discharge.  A traditional generator can go indefinitely, and traditional demand response (kinda sorta) maintains a steady state for a defined period of time.  Depending on type, storage can behave similarly, one exception being batteries.  As batteries charge or discharge, the rate at which they do so tends to change, as does the max voltage available.  Of course we (and dare I say others) make marvelous devices to mitigate the impact of this, but the truth is that batteries never deliver rated capability for the entire span of a charge/discharge cycle.
     
    So the question is whether this should be part of the communications, or whether the grid model learns this via statistical inference from meter data over time.  If the latter, then nothing overt is needed in the comm record.  If the former, then I am at the limit of my ability to expound on this, having attended liberal arts institutions.
     
    Phil


    From: Toby Considine [mailto:tobyconsidine@gmail.com] On Behalf Of Toby Considine
    Sent: Monday, April 26, 2010 12:44 PM
    To: 'David RR Webber (XML)'; 'Edward Cazalet'
    Cc: emix@lists.oasis-open.org; 'Phil Davis'
    Subject: RE: [emix] Power storage strategies

    Push?

    Will that work as well as the Push technologies that are perennially the next wave on the ‘net

    The correct push is appropriate pricing.

    The correct measure of battery efficiency vs afternoon scarcity is pricing.

    tc


    "If something is not worth doing, it`s not worth doing well" - Peter Drucker


    Toby Considine
    TC9, Inc

    OASIS Technical Advisory Board
    TC Chair: oBIX & WS-Calendar

    TC Editor: EMIX, EnergyInterop

      

    Email: Toby.Considine@gmail.com
    Phone: (919)619-2104

    http://www.tcnine.com/
    blog: www.NewDaedalus.com

    From: David RR Webber (XML) [mailto:david@drrw.info]
    Sent: Monday, April 26, 2010 12:36 PM
    To: Edward Cazalet
    Cc: emix@lists.oasis-open.org; Toby.Considine@gmail.com; 'Phil Davis'
    Subject: RE: [emix] Power storage strategies

    Ed,

    Never under estimate an engineers ability to add complexity!

    What is wrong with the simple notion of % full and capacity total in MW and storage ratio?!?!  Completely agnostic to the storage device characteristics!!!

    If I know the storage is 60% full and has a total capacity of 100 MW - and a default ratio of power to storage of 4:1 then I know I can push 40 x 4 = 160 MW at the device to fill it.  Plus if device is sending out updating in intervals - I might send it 100MW - then it says it is 85% full - so I adjust accordingly.

    Once it is full it sends "Stop!" - simple!

    If you want to get clever on your backend systems - you may track actual storage ratio achieved compared to default - or the device can adjust that itself.

    Thanks, DW

    -------- Original Message --------
    Subject: RE: [emix] Power storage strategies
    From: "Edward Cazalet" <ed@MegaWattSF.com>
    Date: Mon, April 26, 2010 12:04 pm
    To: "'David RR Webber (XML)'" <david@drrw.info>, "'Phil Davis'"
    <pddcoo@gmail.com>
    Cc: <emix@lists.oasis-open.org>, <Toby.Considine@gmail.com>

    Phil and David,

     

    Yes, storage can play a big role in providing ancillary services and supporting the integration of wind and solar.  I am a big advocate of distributed storage in very large amounts (see my attached editorial on the subject which has led to pending legislation to promote storage in California).  Also see my storage company's website (www.megawattsf.com) below on this subject.

     

    Both of you raise the issue of what is behind the meters including storage.  After thinking about this problem for some time, I think it is too difficult to communicate what is physically behind the meters.  We would need to know the state of charge of storage devices,  the charge/discharge efficiencies and nonlinearities of each type of battery, battery temperature that can limit use,  and the opportunity costs of storage use.  In some case what is behind the meter changes such as when an electric vehicle is plugged in,  a storage battery is added or removed for maintenance and so on.  And sometimes the storage may be ice storage which is useful when there is an air conditioning load and less useful when there is not air conditioning load. And as David said, each storage device needs new XML.

     

    The other approach is Transactional Energy, wherein the priced offers and transactions over current and forward intervals using frequent, small transactions can fully convey all of the necessary transactional information on what is behind the meter including any storage with no specifics on the devices or their state and no special XML.  And with forward priced offers that form a forward price curve, automated self-dispatch of storage  is much easier to do.

     

    Ed

     

     

    Edward G. Cazalet, Ph.D.

    Vice President and Co-Founder

    MegaWatt Storage Farms, Inc.

    101 First Street, Suite 552

    Los Altos, CA 94022

    650-949-5274

    cell: 408-621-2772

     

    From: David RR Webber (XML) [mailto:david@drrw.info]
    Sent: Monday, April 26, 2010 8:42 AM
    To: Phil Davis
    Cc: emix@lists.oasis-open.org; Toby.Considine@gmail.com
    Subject: RE: [emix] Power storage strategies

     

    Phil,

     

    Can we get one of those 400 people to write some XML for us?!?!

     

     ; -)

     

    If telephone switch industry is a guide here - this means we already have 3 sets of battery subsystem XML - GE, Hitachi and Samsung - with more to follow.  And of course each new model has new XML...

     

    Thanks, DW

    -------- Original Message --------
    Subject: RE: [emix] Power storage strategies
    From: "Phil Davis" <pddcoo@gmail.com>
    Date: Mon, April 26, 2010 11:26 am
    To: "'David RR Webber (XML)'" <david@drrw.info>,
    <Toby.Considine@gmail.com>
    Cc: <emix@lists.oasis-open.org>

    Actually, GE announced such a system last week and is hiring 400 people in Atlanta to staff the new business. It's a substation level product.  Also, I have spoken personally with people at Hitachi and Samsung who are testing a 1 MW battery.  Such a battery from another vendor is in test operation behind PJM's main offices. So local here takes on a new meaning depending on whether it is truly behind the customer meter, or behind the distribution grid meters (substations and the like), or on a transmission system.  Theoretically, batteries of this size could replace generators used for voltage or frequency support.

     

    Phil Davis

     


    From: David RR Webber (XML) [mailto:david@drrw.info]
    Sent: Monday, April 26, 2010 10:58 AM
    To: Toby.Considine@gmail.com
    Cc: emix@lists.oasis-open.org
    Subject: [emix] Power storage strategies

    Toby,

     

    It occurs to me that local storage can potentially play a role here - depending on its efficiency of course.  One can anticipate that future technology will offer higher % there - especially if market forces drive that equation.

     

    Therefore - a future system could offset power surges by drawing on locally stored resources that were captured during off-peak or excess capacity.  In fact such a system may notify suppliers that they can "push" excess power to local storage at some pre-determined cost point - and of course also need to indicate that the storage facility is at a certain % level, or if empty - accept units at a higher cost rate.

     

    DW

     

     


    ________________________________________________________________________
    This email has been scanned for SPAM content and Viruses by the MessageLabs Email Security System.
    ________________________________________________________________________
    --------------------------------------------------------------------- To unsubscribe from this mail list, you must leave the OASIS TC that generates this mail. Follow this link to all your TCs in OASIS at: https://www.oasis-open.org/apps/org/workgroup/portal/my_workgroups.php

    --------------------------------------------------------------------- To unsubscribe from this mail list, you must leave the OASIS TC that generates this mail. Follow this link to all your TCs in OASIS at: https://www.oasis-open.org/apps/org/workgroup/portal/my_workgroups.php



  • 4.  RE: [emix] Power storage strategies

    Posted 04-30-2010 20:16